I know I need to come back with more info as i don`t have the manual with me and I`m unsure of the make on the ac unit on my 98 Regal, but I`m getting a flashing "AAA" code and the unit won`t come on. Any quick ideas?
 
I just had my Marine Air unit replaced with a Cruis Air unit which is supposed to be identical and made on the same assembly line. The manual shows no "AAA" code.

I would either contact the manufacturer or an authorized repair person in your area. They are listed on the manufacturer's website.

In the end, unless it's an electrical or seawater problem, you'll be calling them anyway
 
I1m thinking there is a problem with the led readout showing a bar across the top of the letters and it was really the HHH code. I cleanened the strainer (nothing in it) and snaked the inlet, reset it and it seems to be working fine.
 
quote:

Originally posted by mx8

I1m thinking there is a problem with the led readout showing a bar across the top of the letters and it was really the HHH code. I cleanened the strainer (nothing in it) and snaked the inlet, reset it and it seems to be working fine.






That's good.
 
I agree that the reading was probably HHH which indicates high head pressure which is typically low or no water flow.
 